·The typical measured value of steady-state leakage current of a single-phase module is 5mA.
·The typical measured value of steady-state leakage current of a three-phase module is 20mA.
When multiple parallel operation is adopted on site, if a 30mA leakage protection switch is used, trip may occur.
Suggestions: Recalculate the size of the leakage protection switch based on the actual number of units for parallel operation, then select an appropriate leakage protection switch, or remove the leakage protection switch;
Generally, industrial equipment has reliable and perfect protective grounding, and no additional leakage protection switch is allowed. Moreover, in accordance with national standard requirements (IEC 62368): If the maximum protective conductor current is less than 5% of the input current, it is deemed to meet the product specification requirements.